Problem 1 -

This problem is about a hydroelectric power station in South East Asia operating at 50 Hz. The synchronous generator has the following technical specifications as prescribed by the manufacturer are: rated voltage: 16.5 kV, rated frequency: 50 HZ and rated speed: 500 RPM. The nominal power conditions are P = 50 MW and Q = 75 MVAR. You are appointed as an Electrical Engineer and responsible for the operation of the power station during your shift.

Task 1: Synchronizing with the grid - the rotary valve has been partly opened for water flow and the synchronous generator is brought up to the rated speed. The excitation is adjusted to 32 A such that the generator generates a line voltage of 16.5 KV. The generator's line voltage, frequency, phase sequence, and phase angle are in match with the grid and the synchronizing switch is closed to connect with the grid.

(a) What is the real and reactive power output of the generator? What is the power angle (8) under the mentioned operating conditions?

Task 2: Due to the increase in grid demand, the load dispatching center instructs you to increase real power generation by 25 MW at unity power factor. So the water inlet is increased by controlling the rotary valve to obtain 25 MW power output and simultaneously the field excitation is increased to 38.5 A such that unity power factor is achieved.

(b) What is the power angle (δ) under this condition?

Task 3:

In order to meet the peak hour demand, you are instructed to increase the real power generation to the nominal value of 50 MW.

(c) What is the power angle (δ) under the nominal load condition?

Problem 2 -

A 4160 V, 2500 hp, 2 pole, 3 phase, Y-connected, 3580 rpm, 60 Hz squirrel-cage induction motor is driving a boiler-feed pump. The motor parameters are:

X1 = X2 = 0.72 ohm/phase, Xφ = 3 ohm/phase, neglect all resistances.

Open-circuit transient time constant= 3.6 sec

Short-circuit time constant = 0.12 sec

The motor is operating fully loaded at rated voltage and draws 2160 kVA at 0.9 power factor from the mains.

(a) Compute the transient reactance and draw the constant voltage behind transient reactance model.

(b) Compute the current and E' (magnitude and phase angle).

(c) Determine the time required after interruption of the normal supply for the residual voltage to decay to 25 percent of the normal bus voltage. Note that when the normal source is tripped, flux linkages are "trapped" with the closed rotor circuits of the operating motors, producing a voltage at the terminals (often called the residual voltage) which may require an appropriate time to decay to zero. Determine the speed to which the motor decelerates in this interval (computed in part c). The inertia of the motor and the pump impeller is 76 kg.m2 and the load torque varies as the square of the speed. (Neglect all losses are neglected. 1 hp=746 W.)

Electrical & Electronics, Engineering

  • Category:- Electrical & Electronics
  • Reference No.:- M91979507

Have any Question?


Related Questions in Electrical & Electronics

Question 1for the ce amplifier in figure 1 given the

Question 1 For the CE amplifier in Figure (1), given the following component parameters: Parameter Value β DC , β AC 150 V BE 0 . 7 V V CC 12 V R C 820 ? R E 1 100 ? R E 2 220 ? R 1 20 k? R 2 5 . 2 k? R L 100 k? C 1 , C ...

Question -i a star-connected three-phase synchronous

Question - (i) A star-connected, three-phase synchronous induction motor takes a current of 10 amps from a 415 volt supply at unity power factor when supplying a steady load. If the synchronous reactance is 5 ohms/phase ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

Question 1 in the voltage regulator circuit in figure p221

Question 1: In the voltage regulator circuit in Figure P2.21, V 1 = 20 V, V Z = 10 V, R i = 222Ω and P z (max) = 400 mW. (a) Determine I L, I z , and I L , if R L = 380Ω. (b) Determine the value of R L , that will establ ...

Summative assessmentin 2017 sej101 assessment will consist

Summative Assessment In 2017 SEJ101 assessment will consist of nine tasks that will develop a portfolio of your assessed work. Throughout the trimester you will have the opportunity for feedback on all nine tasks before ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

Case studythis assignment consists of a written report of

CASE STUDY This assignment consists of a written report of approximately 1000 words and any diagrams in which you are asked to critically compare different process methods used to achieve the same result and show an awar ...

Problem 1 a two-phase servomotor has rated voltage applied

Problem 1: A two-phase servomotor has rated voltage applied to its excitation winding. The torque speed characteristic of the motor with Vc = 220 V, 60 Hz applied to its control phase winding is shown in Fig.1. The momen ...

Electrical engineering questions -q1 two ideal voltage

Electrical Engineering Questions - Q1. Two ideal voltage sources designated as machines 1 and 2 are connected, as shown in the figure below. Given E 1 = 65∠0 o V, E 2 = 65∠30 o V, Z = 3Ω. Determine if Machine 1 is genera ...

  • 4,153,160 Questions Asked
  • 13,132 Experts
  • 2,558,936 Questions Answered

Ask Experts for help!!

Looking for Assignment Help?

Start excelling in your Courses, Get help with Assignment

Write us your full requirement for evaluation and you will receive response within 20 minutes turnaround time.

Ask Now Help with Problems, Get a Best Answer

Why might a bank avoid the use of interest rate swaps even

Why might a bank avoid the use of interest rate swaps, even when the institution is exposed to significant interest rate

Describe the difference between zero coupon bonds and

Describe the difference between zero coupon bonds and coupon bonds. Under what conditions will a coupon bond sell at a p

Compute the present value of an annuity of 880 per year

Compute the present value of an annuity of $ 880 per year for 16 years, given a discount rate of 6 percent per annum. As

Compute the present value of an 1150 payment made in ten

Compute the present value of an $1,150 payment made in ten years when the discount rate is 12 percent. (Do not round int

Compute the present value of an annuity of 699 per year

Compute the present value of an annuity of $ 699 per year for 19 years, given a discount rate of 6 percent per annum. As