Ask Electrical & Electronics Expert

Meter Field Testing and Installation Practices

Here, we discuss the installation, commissioning and field testing of meters.

Energy Meters - Installation and Commissioning

The meters are linked before the consumer's isolating device (Main Switch) that might be a moulded case miniature circuit breaker, circuit breaker, or an ironclad switch fuse unit. At the time of commissioning, every meter is tested at site through the owner. A reference standard meter of 0.2 classes or better is used for testing.

Supply Side Wiring

The supply side wiring is the responsibility of the utility and the subsequent must be ensured although carrying it out:

a) The supply wires given are of suitable rating.

b) In case of more than one meter on one service line, it is preferable to use bus-bars. While a number of meters are linked to single distributing mains for registering electricity supplied to various consumer loads, separate service lines - phase(s) and neutral, are used for every meter. Each independently metered consumer load is directly linked to distributing mains by its meter connected in specified phase sequence so as to meet accuracy requirements of relevant standard.

c) The supply wire is properly terminated.

d) The connection is as per links diagram mentioned on meter.

e) Utility should use its own earthing for its devices.

Utility gives phase and neutral supply to the consumers. The neutral is used for carrying return current only. The neutral of one consumer should not be linked to other consumers who have independent and separate supply connection. Utility provides separate neutral to every consumer up the metering point and similar is used through the consumer. The consumer ensures in which all the correct wiring practices are followed and neutral is not looped along with another consumer or meters in the similar premises.  Consumer should not earth the neutral after the metering point. While there are multiple meter installations, bus bar arrangement is used for neutral, so that looping is prevented.

Electrical & Electronics, Engineering

  • Category:- Electrical & Electronics
  • Reference No.:- M9521002

Have any Question?


Related Questions in Electrical & Electronics

Question 1for the ce amplifier in figure 1 given the

Question 1 For the CE amplifier in Figure (1), given the following component parameters: Parameter Value β DC , β AC 150 V BE 0 . 7 V V CC 12 V R C 820 ? R E 1 100 ? R E 2 220 ? R 1 20 k? R 2 5 . 2 k? R L 100 k? C 1 , C ...

Question -i a star-connected three-phase synchronous

Question - (i) A star-connected, three-phase synchronous induction motor takes a current of 10 amps from a 415 volt supply at unity power factor when supplying a steady load. If the synchronous reactance is 5 ohms/phase ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

Question 1 in the voltage regulator circuit in figure p221

Question 1: In the voltage regulator circuit in Figure P2.21, V 1 = 20 V, V Z = 10 V, R i = 222Ω and P z (max) = 400 mW. (a) Determine I L, I z , and I L , if R L = 380Ω. (b) Determine the value of R L , that will establ ...

Summative assessmentin 2017 sej101 assessment will consist

Summative Assessment In 2017 SEJ101 assessment will consist of nine tasks that will develop a portfolio of your assessed work. Throughout the trimester you will have the opportunity for feedback on all nine tasks before ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

1 a name the three major groups of contamination and

1. (a) Name the three major groups of contamination and briefly describe their physical characteristics. (b) Where do the above contamination types come from? Give one example of each. 2. Name two processes metrics which ...

Case studythis assignment consists of a written report of

CASE STUDY This assignment consists of a written report of approximately 1000 words and any diagrams in which you are asked to critically compare different process methods used to achieve the same result and show an awar ...

Problem 1 a two-phase servomotor has rated voltage applied

Problem 1: A two-phase servomotor has rated voltage applied to its excitation winding. The torque speed characteristic of the motor with Vc = 220 V, 60 Hz applied to its control phase winding is shown in Fig.1. The momen ...

Electrical engineering questions -q1 two ideal voltage

Electrical Engineering Questions - Q1. Two ideal voltage sources designated as machines 1 and 2 are connected, as shown in the figure below. Given E 1 = 65∠0 o V, E 2 = 65∠30 o V, Z = 3Ω. Determine if Machine 1 is genera ...

  • 4,153,160 Questions Asked
  • 13,132 Experts
  • 2,558,936 Questions Answered

Ask Experts for help!!

Looking for Assignment Help?

Start excelling in your Courses, Get help with Assignment

Write us your full requirement for evaluation and you will receive response within 20 minutes turnaround time.

Ask Now Help with Problems, Get a Best Answer

Why might a bank avoid the use of interest rate swaps even

Why might a bank avoid the use of interest rate swaps, even when the institution is exposed to significant interest rate

Describe the difference between zero coupon bonds and

Describe the difference between zero coupon bonds and coupon bonds. Under what conditions will a coupon bond sell at a p

Compute the present value of an annuity of 880 per year

Compute the present value of an annuity of $ 880 per year for 16 years, given a discount rate of 6 percent per annum. As

Compute the present value of an 1150 payment made in ten

Compute the present value of an $1,150 payment made in ten years when the discount rate is 12 percent. (Do not round int

Compute the present value of an annuity of 699 per year

Compute the present value of an annuity of $ 699 per year for 19 years, given a discount rate of 6 percent per annum. As