Power companies have to maintain the rms voltage level at each customer's location. Assume the acceptable deviation is +- 5.8%. Thus, a nominal rms voltage of 120 V will range from 113 to 127 V. Suppose the line to line voltage at Customer A is 13.8kV, the load at customerA consumes complex power (1.2+j1.2)x 10^6 W.
Customer A is connected to a power plant via a three-phase line and each phase line has the impedance of 1.8+j14.4.
a) What line to line voltage at the plant is needed to generate a line to line voltage of 13.8 kV at the customer.
b) Could the voltage create problems for other customers requiring 13.8V?