Assignment: PROTECTION PROJECT

 

1. Problem and Report

 

Enclosed as Figure 1 is a diagram of an Arizona looped 230 kV transmission system which is typical of a system serving a large city. There is remote generation whose power is input to the loop over 2 - 345 kV lines. The voltage is transformed from 345 kV to 230 kV by 3-phase transformer banks T3 and T4. Transformer T1 and T2 step the voltage up at the remote generating site. Figure 2 is a single line diagram of the 230 kV and 345 kV systems, including the series impedance. Note that the data is in per unit on a 100 MVA base, 230 kV and 345 kV bases. The generator and transformer data is given in Section 2.

 

1456_Topology-and-for-a-Looped-Transmission-System.jpg

 

848_Signal-Line-Diagram-for-System.jpg

 

The Project is divided into 3 parts as follows:

 

1.0 Build the above system using PowerWorld

 

Build a simulation of the above system using PowerWorld.

 

1.1 Time-Over-Current Relay Scheme for a 69 kV Radial System

 

Design a coordinated time-over-current relay scheme for the radial 69 kV system shown in Figure 3. This radial system is connected to bus 5 of the system shown in Figures 1 and 2. The 69 kV structure configuration and line data is shown in Figure 4. Assume the zero sequence impedance is three times the positive sequence impedance. For minimum fault current calculations assume that the line from bus 5 and bus 9 is out.

 

Include:

 

The necessary short circuit studies.

 

The breaker ratings for B11-B13.

 

The CT ratios associated with B11-B13.

 

The tap and time dial settings for CO-8 relays associated with B11-B13.

 

The basis for the selections in the form of a report.

 

395_Radial-System-Schmatic.jpg

 

2413_69-k-V-Line-Layout.jpg

 

Figure 4. 69kV line layout.

 

1.2 Distance Relay Protection System

 

Design a distance (impedance) protection system to protect the 230 kV line between busses 5 and 9 and to provide remote backup protection for line from bus 5 to bus 6. The 230 kV lines have 954 KCM ACSR conductors. You will need both an impedance ground fault relay and an impedance phase relay. Use mho units.

 

Include:

 

Circuit breaker selection.

 

Instrument transformer selection and connections.

 

Relay selections and settings.

 

Validation of your settings for all fault types by calculating the apparent impedance at bus 9 from computer studies for faults at bus 5. Revise your initial settings, if required.

 

The basis for the selections in the form of an engineering report.

 

Pertinent computer studies.

 

2. Generator and Transformer Data

 

Gen. No.      MVA          kV___    ____x"d=X1=X2__    _____x0______      Connection
      1          333         22kV          .08 pu                       .10 pu                       Note 2
      2             "              "               "                                "                              "
      3          210         230kV       .14 pu (Note 1)         .24 pu (Note 1)         Note 3
      4            "             "                "                               "                              "
      5            "             "                "                               "                              "
      6          353           "             .34 pu (Note 1)         .28 pu (Note 1)             "
      7            "             "                "                               "                              "

 

 

Notes:

 

1. This impedance includes the step-up transformer impedance on the generator MVA bases.

 

2. Ungrounded wye for generators 1 and 2.

 

3. Assume generators are connected grounded wye and the generator step-up transformers are connected grounded wye - grounded wye.

 

Transformers:

 

Transformers 1 and 2 are 3-phase rated at 350 MVA, 22 kV delta to 345 kV grounded wye, 8% reactance.

 

Transformers 3 and 4 are 3-phase rated at 400 MVA, 345 kV grounded wye to 230 kV grounded wye, 6% reactance

 

The template for the report is included in a separate file. Include all the material asked for in the project in the provided template.

 

Other Engineering, Engineering

  • Category:- Other Engineering
  • Reference No.:- M92528015

Have any Question?


Related Questions in Other Engineering

Task 1using the lab kit design a circuit for the processor

Task 1: Using the lab kit, design a circuit for the processor to control the output of a connected 7-segment LED display device. You will be provided with a standard common anode 7-segment display of the type FND-507 (or ...

Assessment practical reportproduce a short technical report

Assessment: Practical Report Produce a short technical report in a form consistent with proteomic journals covering the techniques, results and interpretation of your proteomics experiment in the practical classes. The r ...

Mine safety amp environmental engineeringpart 1 questions1

Mine Safety & Environmental Engineering Part 1. Questions 1. Occupational health and safety is the primary factor that needs to be considered in the mining industry. Discuss this statement. 2. Define the following terms ...

Question - show that the zero-point energy of a simple

Question - Show that the zero-point energy of a simple harmonic oscillator does not contribute to its entropy or heat capacity, but does contribute to its energy and Helmholtz function.

Assignment 11 what is the purpose of ore reserve and

ASSIGNMENT 1 1. What is the purpose of ore reserve and resource estimation? Why are resource and reserve estimates important to the mining industry? 2. What is meant by ore? What is meant by the term waste? How is the di ...

Control theory - lab reportsfor experiments 1 to 4 you must

Control Theory - Lab Reports For experiments 1 to 4 you must undertake the following: a) At the start of each section (including the pre-lab activities) there are a number learning outcomes. That is, what students should ...

Register design a cpu register is simply a row of

Register design A CPU register is simply a row of flip-flops (i.e. SR, JK, T, etc) put side by side in an array to make the size of register required. For example, an 8 bit register has 8 flip-flops side by side for stor ...

Operations engineering assignment -please select only one

Operations Engineering Assignment - Please select only one of the following case studies for your assignment: CASE A. Tesla Motors Tesla is an innovative manufacturer that designs, assemble and sells fully electric vehic ...

Engineering analysis assignment -for every problem provide

Engineering Analysis Assignment - For every problem, provide The MATLAB script/function files that solve the problems. Problem 1: Plot the function f(t) = (x+5) 2 /(4+3x 2 ) for -3 ≤ x ≤ 5. using plot command. Use the ar ...

  • 4,153,160 Questions Asked
  • 13,132 Experts
  • 2,558,936 Questions Answered

Ask Experts for help!!

Looking for Assignment Help?

Start excelling in your Courses, Get help with Assignment

Write us your full requirement for evaluation and you will receive response within 20 minutes turnaround time.

Ask Now Help with Problems, Get a Best Answer

Why might a bank avoid the use of interest rate swaps even

Why might a bank avoid the use of interest rate swaps, even when the institution is exposed to significant interest rate

Describe the difference between zero coupon bonds and

Describe the difference between zero coupon bonds and coupon bonds. Under what conditions will a coupon bond sell at a p

Compute the present value of an annuity of 880 per year

Compute the present value of an annuity of $ 880 per year for 16 years, given a discount rate of 6 percent per annum. As

Compute the present value of an 1150 payment made in ten

Compute the present value of an $1,150 payment made in ten years when the discount rate is 12 percent. (Do not round int

Compute the present value of an annuity of 699 per year

Compute the present value of an annuity of $ 699 per year for 19 years, given a discount rate of 6 percent per annum. As